    RCD Tripping After Rain

    A couple of times recently after or during heavy rain, the RCD in the circuit box in our hall has tripped, taking out all of the three-pin sockets. The curious thing is that it seems only to trip when the gas boiler is on. At the moment for example the RCD switch is back in position and, with the boiler switched off, it will stay put indefinitely.

    There is an electrical socket on the wall outside and it's possible that water has got into that, because the cover has deteriorated. But while the boiler is off the RCD doesn't trip. Turning it back on while the boiler is on will make it trip within 5-10 mins (until the rain's stopped for a while and presumably something has dried out).

    There's no sign of water ingress near the boiler and the flue that comes through the external wall it's attached to is in the same condition it's been in since we moved here in 2009; it has a little rain canopy and that hasn't deteriorated at all.

    It doesn't happen at all during dry weather.

    Any thoughts, anyone? Is it plausible that a damp external mains socket could make the RCD more sensitive to being tripped by the boiler?

  2. #2
    Master
    Join Date
    Aug 2017
    Location
    London, UK
    Posts
    3,009
    I’ve just been through this and it was traced to an external light with an IR sensor. Moisture was tripping RCD.

    The electrician did load testing to find it. Apologies, no idea what load testing is !

  3. #3
    Master
    Join Date
    Dec 2010
    Location
    NW Leics
    Posts
    8,653
    Thanks Joe, it's just that the boiler seems to trip it that doesn't seem to fit the hypothesis that it's something exposed outside that's to blame. How much did the electrician cost, if you don't mind me asking?

  4. #4
    How old is your boiler? It’s possible it has a fault or that the boiler is using the earth as a switched live if it’s been replaced in situ and that is grounding out (ours was like this, had an RF link put in to reinstate the earth and enable pump overrun).
    "Bite my shiny metal ass."
    - Bender Bending Rodríguez

  5. #5
    Master
    Join Date
    Aug 2017
    Location
    London, UK
    Posts
    3,009
    Quote Originally Posted by monogroover View Post
    Thanks Joe, it's just that the boiler seems to trip it that doesn't seem to fit the hypothesis that it's something exposed outside that's to blame. How much did the electrician cost, if you don't mind me asking?
    He refused to accept any money, he’s a village local and wanted to help. If it helps, I’d say it took him an hour.

  6. #6
    Master
    Join Date
    Dec 2010
    Location
    NW Leics
    Posts
    8,653
    Quote Originally Posted by stooo View Post
    How old is your boiler? It’s possible it has a fault or that the boiler is using the earth as a switched live if it’s been replaced in situ and that is grounding out (ours was like this, had an RF link put in to reinstate the earth and enable pump overrun).
    The boiler's the same age as the house, about 20 years I think. It does get serviced every two or three years. There's definitely been no change to the way it's wired in the last 15 years, but the RCD tripping issue has only happened in the last two weeks.

  7. #7
    Master
    Join Date
    Aug 2010
    Location
    Kent
    Posts
    7,715
    Could be just a coincidence- I’d swap out that exterior socket asap and make sure it watertight
    That then would elimate that

  8. #8
    Grand Master
    Join Date
    Nov 2011
    Location
    Berkshire
    Posts
    10,874

    RCD Tripping After Rain

    Christ this needs to be not here.

    So many comments on investment or lack of over the years.


    Sent from my iPad using Tapatalk
    Last edited by Mj2k; 5th December 2024 at 07:43.

  9. #9
    Craftsman
    Join Date
    Sep 2006
    Location
    SW London
    Posts
    329
    This might make the circuit more sensitive, especially when the boiler is drawing power.

  10. #10
    Master gunner's Avatar
    Join Date
    Aug 2008
    Location
    Kent
    Posts
    5,140
    I'd check the flue too, might be letting water back in which trips the boiler.

  11. #11
    Grand Master Onelasttime's Avatar
    Join Date
    Oct 2014
    Location
    Everywhere, yet nowhere...
    Posts
    14,904
    Quote Originally Posted by Mj2k View Post
    Christ this needs to be not here.

    So many comments on investment or lack of over the years.


    Sent from my iPad using Tapatalk
    Wrong thread?

  12. #12
    Master jools's Avatar
    Join Date
    Jan 2007
    Location
    Île de Merde
    Posts
    5,258
    You might have more than one appliance/socket/wiring junction with a small earth leak which, when all in use, together take the leakage over the limit of 30ma or whatever it is.

  13. #13
    Master
    Join Date
    Dec 2010
    Location
    NW Leics
    Posts
    8,653
    Thanks a lot for the replies. There's no problem running fan heaters and a washing machine off the same circuit, but the gas boiler, which I think uses less electrical power than any of those will trip the RCD as soon as I switch the hot water on at the moment. Even with the other appliances switched off.

  14. #14
    Master
    Join Date
    Jan 2011
    Location
    Maidenhead-ish UK
    Posts
    1,550
    Quote Originally Posted by monogroover View Post
    Thanks a lot for the replies. There's no problem running fan heaters and a washing machine off the same circuit, but the gas boiler, which I think uses less electrical power than any of those will trip the RCD as soon as I switch the hot water on at the moment. Even with the other appliances switched off.
    It's not the consumption that is relevant, it's the amount of earth leakage. If the boiler is leaking 10mA to earth the the RCD won't trip but if the rain fault adds another 25mA this will take the total to over 30mA & the RCD will trip. You need a sparky who can measure the earth currents & find the cause of the rain induced leakage. Outside sockets are always a good starting point.

  15. #15
    Master sweets's Avatar
    Join Date
    Jan 2007
    Location
    Bristol - UK
    Posts
    6,283
    As you know the external socket has a fault, I see no problem with replacing that for starters.

    A gas boiler is also relatively unique in having a high voltage spark ignition (I take it that it does, rather than a pilot light). Something very few other appliances have.
    This can be relatively noisey on the earth and therefore trip an RCD if its own earth connection is poor, or if there is other contributory faults (like the possibility of the external socket leaking).
    Even if your boiler doesn't spark, your observations suggest that there might be a fault in the boiler too.
    So I would guess that one fault on its own was not the problem, but when a second started, the two together make earth leakage big enough to trip the RCD.
    You could go through all of this, but a professional will do it better, and quicker as they will have all the right metering kit to isolate the source of the fault(s)

  16. #16
    Master
    Join Date
    Dec 2010
    Location
    NW Leics
    Posts
    8,653
    Quote Originally Posted by sweets View Post
    As you know the external socket has a fault, I see no problem with replacing that for starters.

    A gas boiler is also relatively unique in having a high voltage spark ignition (I take it that it does, rather than a pilot light). Something very few other appliances have.
    This can be relatively noisey on the earth and therefore trip an RCD if its own earth connection is poor, or if there is other contributory faults (like the possibility of the external socket leaking).)
    Thank-you - that is a plausible working hypothesis because I can't see how moisture from rain can be interfering with the boiler. For now I've sealed up the cover on the external socket with plastic ties and plastic. I will have it replaced, or isolated in the short term to see what happens.

  17. #17
    If water gets into flue will only end up in combustion chamber and this should have gas-tight seal to rest of boiler (and dangerous if not).

  18. #18
    Craftsman
    Join Date
    Apr 2016
    Location
    In them there mountainous Hills of Surrey
    Posts
    362
    Quote Originally Posted by Mr Pointy View Post
    It's not the consumption that is relevant, it's the amount of earth leakage. If the boiler is leaking 10mA to earth the the RCD won't trip but if the rain fault adds another 25mA this will take the total to over 30mA & the RCD will trip. You need a sparky who can measure the earth currents & find the cause of the rain induced leakage. Outside sockets are always a good starting point.
    This sounds about right to me. Where you have a single RCB covering a number of outgoing circuits the RCB ‘sees’ the cumulative total of earth leakage from all the circuits. It very easy for that cumulative total to exceed 30mA and trip the RCB even when no single circuit’s leakage is bad enough on its own. This is why modern (18th edition) consumer units are no longer split load (half RCB protected and half not) and every applicable final circuit now gets its own individual RCB protection using RCBO or AFDD breakers, meaning the cumulative total is no longer a consideration.

  19. #19
    Replace the outside socket, making sure the back is sealed - that's an easy DIY job.

    If it still trips then call an electrician to locate the fault.

  20. #20
    Master
    Join Date
    Dec 2010
    Location
    NW Leics
    Posts
    8,653
    Many thanks for all the replies, appreciate the help and advice. A heating engineer has replaced a pump that had seized - and the boiler can now be switched on without tripping the RCD. I'm still a bit uneasy about the correlation to the behaviour with wet weather, but there's no doubt that the boiler is working at the moment, it chucked down all day yesterday and there was rain this morning. So I'm hopeful.

    The external socket has been carefully waterproofed using plastic sheet and plastic ties and it will be replaced in any case.