    Down lighter transformer melted!

    Had an extension built 14 years ago and had halogen downlighting fitted and up until now just the odd halogen bulb has gone, recently though two lights have stopped working, I change the bulbs but they still didn’t work so today I decided to investigate further.
    This is what I found......
    One had a dimple melted into the
    transformer and also one side of the connection block had melted
    The other had a very blackened connection block.
    Is this normal?
    I have now replaced everything in the chain from the feed to the bulbs.
    Last edited by dizz; 6th October 2018 at 17:04.

  2. #2
    Master
    Join Date
    May 2011
    Location
    Eastern England
    Posts
    3,113
    Any poor connection can lead to resistance and overheating. Poor connections can be due to loose or corroded connections or wires. Kitchen wiring can get damp due to steamy conditions over cookers/kettles etc. Also check for dampness in the ceiling/roof area.

  3. #3
    Master IAmATeaf's Avatar
    Join Date
    Nov 2011
    Location
    NW London
    Posts
    4,757
    It looks like one of the plastic connectors was resting on the transformer so melted. Ideal time to replace the lot with modern mains poweredl leds I think ?

  4. #4
    Grand Master Mr Curta's Avatar
    Join Date
    May 2014
    Location
    Mainly UK
    Posts
    17,354
    Often happens with Low Voltage Halogens, they are downright dangerous if not installed properly. Go for LEDs.

  5. #5
    Master
    Join Date
    Jul 2008
    Location
    Surrey England
    Posts
    1,688
    Quote Originally Posted by IAmATeaf View Post
    It looks like one of the plastic connectors was resting on the transformer so melted. Ideal time to replace the lot with modern mains poweredl leds I think ?
    I think your spot on there.


    Sent from my iPad using Tapatalk

  6. #6
    Master RLE's Avatar
    Join Date
    Mar 2009
    Location
    UK
    Posts
    2,912
    Quote Originally Posted by Mr Curta View Post
    Often happens with Low Voltage Halogens, they are downright dangerous if not installed properly. Go for LEDs.
    Echo this. We had similar issues with one in the bathroom despite being fitted by qualified electricians. All good and well having the cone suppressor over the lights to isolate potential fire risks due to the heat generated, but they are hardly beneficial when the transformers are overheating.

    LEDs do away with the transformers, yet to have a bulb blow, low heat etc. Upgrade time.

  7. #7
    Master
    Join Date
    Apr 2006
    Location
    Berkshire
    Posts
    5,115
    We've had the same kind of problem before, and its normally down to the transformer being in contact with something.
    I'm thinking of replacing all the transformer downlighter with led mains powered ones.

  8. #8
    Master IAmATeaf's Avatar
    Join Date
    Nov 2011
    Location
    NW London
    Posts
    4,757
    The problem with these transformers is that no matter who fits them unless they are screwed to something they will move from where they’ve been placed as you push the lit fitting in.

    I had similar on 2 of mine so a few years ago dumped them all and replaced them with leds.

  9. #9
    don't forget that you can't use loft/cavity insulation in close proximity or they will overheat.....

  10. #10
    Are burnt connectors on the AC or DC side?

  11. #11
    Grand Master Chris_in_the_UK's Avatar
    Join Date
    Nov 2004
    Location
    Norf Yorks
    Posts
    43,008
    Quote Originally Posted by Mr Curta View Post
    Often happens with Low Voltage Halogens, they are downright dangerous if not installed properly. Go for LEDs.
    2nd this.
    When you look long into an abyss, the abyss looks long into you.........

  12. #12
    Master
    Join Date
    Jul 2008
    Location
    Surrey England
    Posts
    1,688

    Down lighter transformer melted!

    Quote Originally Posted by adrianw View Post
    Are burnt connectors on the AC or DC side?
    Light 1
    The melted connector was before the transformer.

    Light 2
    The burnt/blackened connector was after the transformer (between the transformer and the bulb)


    Sent from my iPad using Tapatalk
    Last edited by dizz; 7th October 2018 at 14:13.

  13. #13
    Master hhhh's Avatar
    Join Date
    Sep 2009
    Location
    Cloud 9
    Posts
    4,297
    Quote Originally Posted by IAmATeaf View Post
    mains poweredl leds I think ?
    Definitely the way to go.

  14. #14
    Master
    Join Date
    Jun 2005
    Location
    Stoke-on-Trent
    Posts
    1,820
    Quote Originally Posted by Mr Curta View Post
    Often happens with Low Voltage Halogens, they are downright dangerous if not installed properly. Go for LEDs.
    I agree, we now have them in both our kitchen and bathroom. They seem to last longer and they definitely consume a great deal less electricity.


    Sent from my iPhone using TZ-UK mobile app

  15. #15
    in the day when I had AC/DC converted halogen ones in my bathroom and kitchen I remember using ceramic connecting blocks - they act like a heatsink
    looks like those are standard plastic ones which have melted causing the issue

    use LEDS / ceramic blocks - makes sure they dont touch the transformers, maybe find transformers with heatsinks on them if yours are getting too hot

    Last edited by Xantiagib; 9th October 2018 at 10:27.

  16. #16
    Craftsman
    Join Date
    Jan 2015
    Location
    Ruislip, UK
    Posts
    983
    Some of the more expensive transformers have a thermal cut out built in. Did the fitting work intermittently for a time?

    I would advise any one with 12v halogen down lights to replace with LED.

    The old LV halogens produce too much heat and end up baking the components around them over time. Before LED became popular I would always advise against using 50 watt 12v lamps and suggest using 35 watt or even 20 watt Aluminuim backed lamps that direct the heat downward along side ceramic connectors. The very cheap 50w LV lamps push a lot of heat upward.

    You will also appreciate the energy saving over a year - 50w of halogen v 5w of LED - you don't have to be a mathematician.

    It's quite an easy fix to replace LV with mains voltage LED. An electrician shouldn't charge too much or if you feel confident have a go yourself, just be safe.

  17. #17
    Journeyman Mathif's Avatar
    Join Date
    Mar 2016
    Location
    Bishop's stortford
    Posts
    202
    Lose cable or too thin cable...


    Sent from my iPhone using TZ-UK mobile app

  18. #18
    Master IAmATeaf's Avatar
    Join Date
    Nov 2011
    Location
    NW London
    Posts
    4,757
    Quote Originally Posted by Mathif View Post
    Lose cable or too thin cable...


    Sent from my iPhone using TZ-UK mobile app
    Did you read the entire thread?

  19. #19
    Master
    Join Date
    Jul 2008
    Location
    Surrey England
    Posts
    1,688
    The lights just failed without warning over about a six months period (kept putting of investigating) they were fitted when the extension was built around fourteen years ago, so fitted ok by the election, it’s just old age of the units that’s causing them to fail.

    I am considering changing the main kitchen lights (8x 50w halogen) to LEDs as they are on the most and therefore use the most power. Seems the best bet is to do away with the transformers altogether and go mains power driven.
    I’m looking at all in one LED lamp units but it’s a bit of a mine field, colour temp, wattage choice, manufacturer etc.
    Any electrical savvy people who have done this conversation recently (LED technology moves on quickly it seems) who can advise me where to start please?


    Sent from my iPad using Tapatalk

  20. #20
    Master IAmATeaf's Avatar
    Join Date
    Nov 2011
    Location
    NW London
    Posts
    4,757

    Down lighter transformer melted!

    I ended up replacing both the existing down lighters housings and the bulbs. Reason for doing this was the previous housing that my builder fitted were open which I didn’t know so changed them out for something fully enclosed and supposedly much safer.

    For the bulbs and I know they get slated, I ended up with Aurora Enlite bulbs as a friend in the know recommended them and to date they’ve been fine.
    Last edited by IAmATeaf; 14th October 2018 at 21:09.

  21. #21
    Craftsman
    Join Date
    Feb 2012
    Location
    Surrey
    Posts
    482
    We’ve fitted close to 600 Of these. Very quick they come with the plugs and the lights have the socket intergrated which makes them extremely quick to change. Spread of light is good with a 60 degree beam angle. You can change the bezels separately from the fitting so can match them to an existing style.

    http://enlitelighting.com/gb/ProductDetail/EN-DE6PRO