    Combi boiler condensate line freezing!!

    Got up this morning, ran the hot water tap and couldn't get hot water, at this point my day started to go downhill. Central heating boiler problems are an absolute pain, always occur at the least convenient time and like many I rely totally on a combi boiler to provide heating and hot water so when it packs up I`m screwed. Boiler's only 18 months old, problem turned out to be the condensate drain line blocked solid with bloody ice. Fortunately it's v. easy to get to, with approx. 3 feet running vertically down the bungalow wall into a drain. 15 mins with a hair dryer fixed it and the boiler's now running OK again.



    What I can`t work out is how to prevent this happening again, ideally the condensate line could've been run into the drain pipe from the dishwasher indoors, but now the kitchen's been refitted it's a sizeable job to modify so I`m stuck with the vertical pipe outside. Thought about lagging it but I`m not convinced it'll help, the temperature of the line follows the ambient cycle, warming above freezing (usually) in the daytime and dropping at night, if it's lagged it won't warm up as readily.

    After a couple of days of sub-zero temperatures with no sunlight the line has blocked and I see no reason why it won't happen again, despite it being a simple problem to understand I`m struggling to find a solution.

    If this was in an industrial setting the line would be trace heated and lagged, problem solved, I find domestic plumbing frustrating in this respect !.

    All suggestions welcome. Modifying the line to make it easy to dismantle and allow the condensate to drip freely when the temp is sub-zero is one answer but it's hardly subtle.

  2. #2
    Is the ice in the vertical section or the near horizontal part?

    Fit a wider bore pipe if the former.

  3. #3
    You could get someone to fit some type of heat tracing.


    Sent from my iPhone using Tapatalk

  4. #4
    Master
    Join Date
    Nov 2011
    Location
    Berkshire
    Posts
    9,336
    For the price of a piece of lagging, I’d give it a try first. Whilst it won’t warm as quickly, it may be just enough to keep the temp above freezing inside, so then won’t have to thaw.

    Modification to remove bad required would be my other approach, but only if needed.

    It’s not all great having it inside either. Ours had a slight leak at a joint & required so many pieces of kitchen cupboards to access as was behind the cabinet and of course in the tightest, hardest to reach place.

    As an aside, would a kettle be quicker than a hair dryer? Having just used the layer to melt the ice on my car window so it would drop as I left the handle and clear itself from the roof, it seemed to take forever.

  5. #5
    Master blackal's Avatar
    Join Date
    Mar 2012
    Location
    Scottish Borders
    Posts
    9,796
    Lag it, and run some heat-trace down the inside (from inside at the boiler - down as far as you can inside 2-3m of cable will do. Use a timer on the plug, but it is self-regulating anyway.

    But, I would run the tail of the heat-trace out the bottom of the pipe and seal the exit. Reason is that the condensate is mildly acidic - so you may have trouble sealing the end of the heat-trace against that.

    https://www.ebay.co.uk/itm/122049395...Bk9SR4qEs-WiYQ

  6. #6
    Master
    Join Date
    Aug 2010
    Location
    Kent
    Posts
    7,282
    Could you construct a crude wooden (temp) oblong box filled with loft insulation to cover the pipe during the couple of months it’s that cold?
    Or a length on white guttering filled with insulation with an end cap on the top?

  7. #7
    Grand Master
    Join Date
    Jul 2007
    Location
    Wakefield, West Yorkshire
    Posts
    22,521
    It appears there are some trace heating kits that are OK to use with plastic pipes, something simple that can be controlled from the kitchen would suffice but the fridge freezer will need taking out to fit. Id prefer something low voltage running off a transformer but haven`t found anything. Anything using direct 240v needs doing carefully and thinking about.

    Judging from the icicles that came out, the pipe definitely froze in the vertical section.

    Pouring hot water on the pipe is a way of clearing it but there's a risk of cracking the plastic due to thermal stress. I was surprised how much ice had formed, I think it's built up over a few days. Took a while to fully thaw out, plastic's a poor conductor of heat so I ended up using the hair dryer for a good 10 mins. Not ideal.

    Might try some lagging and gaffer tape as a short-term measure. By coincidence I've spent the last 2 days lagging central heating pipes in the loft to eliminate heat losses, the pipe runs are approx. 25' and weren't lagged as thoroughly as they should be when the boiler was fitted. One of these jobs I`ve been putting off doing for a while.

  8. #8
    Master blackal's Avatar
    Join Date
    Mar 2012
    Location
    Scottish Borders
    Posts
    9,796
    Make sure any lagging is waterproof closed cell.

  9. #9
    Master reggie747's Avatar
    Join Date
    Oct 2013
    Location
    The Mersey Riviera
    Posts
    7,214
    As has been said above, as early as possible in the run, use a larger diameter pipe, 32mm waste pipe will suffice.

  10. #10
    Master Ruggertech's Avatar
    Join Date
    Jun 2019
    Location
    Deepest darkest South Wales.
    Posts
    7,210
    Assuming it's the nearest pipe in your photo that's looks like a smaller bore than usual. Less diameter equal less ice build up to block it maybe?
    Mine blocked during the beast from the east, but it followed a very shallow path from our attic to the rainwater gutter. The problem was ice forming in the gutter like a stalagmite from the pipe outlet which ultimately built up and into the pipe. I couldn't stop it reoccurring except by sawing the pipe off before it reached the gutter, the only remedy actually during the storm. Still a nightmare job up a ladder durimg that storm.
    Its completely rerouted now and stops about 4 inches above a drain, so far so good.

  11. #11
    Master
    Join Date
    Aug 2010
    Location
    Kent
    Posts
    7,282
    Quote Originally Posted by Ruggertech View Post
    Assuming it's the nearest pipe in your photo that's looks like a smaller bore than usual. Less diameter equal less ice build up to block it maybe?
    Mine blocked during the beast from the east, but it followed a very shallow path from our attic to the rainwater gutter. The problem was ice forming in the gutter like a stalagmite from the pipe outlet which ultimately built up and into the pipe. I couldn't stop it reoccurring except by sawing the pipe off before it reached the gutter, the only remedy actually during the storm. Still a nightmare job up a ladder durimg that storm.
    Its completely rerouted now and stops about 4 inches above a drain, so far so good.
    That’s the correct size for the condensation pipe- maybe yours is a different pipe- but if it’s is the condensation pipe it shouldn’t (I believe) be routed into the gutter

  12. #12
    Master
    Join Date
    Oct 2019
    Location
    East Anglia
    Posts
    1,854
    Blog Entries
    2
    Move the pipe inside

  13. #13
    I had that problem for years. Thought we solved it last winter with much larger diameter pipe. Minus 12 in Manchester last night meant that isn’t a solution. It was lagged as well. Was at B&Q by 8 am. Got the fitting closest to the boiler pulled apart and added a new fitting and pipe that dangles inside to a bucket. Fills quite slowly and a temporary fix whilst we suffer this very cold spell


    Sent from my iPhone using TZ-UK mobile app

  14. #14
    Grand Master Chris_in_the_UK's Avatar
    Join Date
    Nov 2004
    Location
    Norf Yorks
    Posts
    43,040
    Ours is a 32mm diameter pipe with a condensate trap on the inside - never had any issues.
    When you look long into an abyss, the abyss looks long into you.........

  15. #15
    Grand Master oldoakknives's Avatar
    Join Date
    Sep 2012
    Location
    United Kingdom
    Posts
    20,210
    Blog Entries
    1
    Cant it join the other pipe inside, before it goes through the wall?
    Started out with nothing. Still have most of it left.

  16. #16
    Master
    Join Date
    Jan 2017
    Location
    Wolverhampton
    Posts
    4,232
    We've already done this in the Check your outside pipes thread:

    https://forum.tz-uk.com/showthread.p...-outside-pipes

    If you tee-off your run-off pipe from the boiler into a container of some sort it will eradicate the problem. When the outside feedout is blocked by ice the condensate has nowhere to go so this mod is a failsafe costing pennies. I'm just waiting for a pic to illustrate the solution.



    It goes into the bucket. Be careful because the resultant liquid is acidic.
    Last edited by Harry Smith; 15th December 2022 at 17:54.

  17. #17
    Master
    Join Date
    Jul 2016
    Location
    West Yorks
    Posts
    1,279
    Quote Originally Posted by Harry Smith View Post
    We've already done this in the Check your outside pipes thread:

    https://forum.tz-uk.com/showthread.p...-outside-pipes

    If you tee-off your run-off pipe from the boiler into a container of some sort it will eradicate the problem. When the outside feedout is blocked by ice the condensate has nowhere to go so this mod is a failsafe costing pennies. I'm just waiting for a pic to illustrate the solution.



    It goes into the bucket. Be careful because the resultant liquid is acidic.
    .


    Thats the get out of jail card right there,

  18. #18
    Grand Master learningtofly's Avatar
    Join Date
    Jul 2010
    Location
    Everywhere & nowhere, baby
    Posts
    37,607
    Quote Originally Posted by Harry Smith View Post
    We've already done this in the Check your outside pipes thread:

    https://forum.tz-uk.com/showthread.p...-outside-pipes

    If you tee-off your run-off pipe from the boiler into a container of some sort it will eradicate the problem. When the outside feedout is blocked by ice the condensate has nowhere to go so this mod is a failsafe costing pennies. I'm just waiting for a pic to illustrate the solution.



    It goes into the bucket. Be careful because the resultant liquid is acidic.
    Why the step up - is that a requirement?

  19. #19
    Master
    Join Date
    Jan 2017
    Location
    Wolverhampton
    Posts
    4,232
    Quote Originally Posted by learningtofly View Post
    Why the step up - is that a requirement?
    The plumber (aka heating guru) said it was to encourage the condensate to take it's normal route in warmer weather or you would be constantly emptying ze bucket dear liza.

  20. #20
    Grand Master learningtofly's Avatar
    Join Date
    Jul 2010
    Location
    Everywhere & nowhere, baby
    Posts
    37,607
    Quote Originally Posted by Harry Smith View Post
    The plumber (aka heating guru) said it was to encourage the condensate to take it's normal route in warmer weather or you would be constantly emptying ze bucket dear liza.
    Ah, got you, thanks.

  21. #21
    Craftsman
    Join Date
    Dec 2012
    Location
    Hampshire
    Posts
    459
    I used the grey foam pipe lagging you can buy at diy stores at my last house. Changed the lagging after 6 years when it started deteriorating. Never had an issue in the eight years we were there.

  22. #22
    Master
    Join Date
    Aug 2013
    Location
    London
    Posts
    2,259
    Is there not a minimum diameter now to stop exactly this and that looks too thin.

  23. #23
    Quote Originally Posted by Harry Smith View Post
    We've already done this in the Check your outside pipes thread:

    https://forum.tz-uk.com/showthread.p...-outside-pipes

    If you tee-off your run-off pipe from the boiler into a container of some sort it will eradicate the problem. When the outside feedout is blocked by ice the condensate has nowhere to go so this mod is a failsafe costing pennies. I'm just waiting for a pic to illustrate the solution.



    It goes into the bucket. Be careful because the resultant liquid is acidic.
    Don’t think I’d get away with a bucket in the kitchen but good idea if boiler elsewhere.

  24. #24
    Grand Master learningtofly's Avatar
    Join Date
    Jul 2010
    Location
    Everywhere & nowhere, baby
    Posts
    37,607
    Quote Originally Posted by Kingstepper View Post
    Don’t think I’d get away with a bucket in the kitchen but good idea if boiler elsewhere.
    My boiler's in a wall-mounted kitchen cupboard with little room below, so that would be a challenge too!

  25. #25
    Master
    Join Date
    Jan 2017
    Location
    Wolverhampton
    Posts
    4,232
    Quote Originally Posted by Kingstepper View Post
    Don’t think I’d get away with a bucket in the kitchen but good idea if boiler elsewhere.
    Not obvious in the pic but the boiler is in a bi-fold door-ed understairs cupboard, so not unsightly at all.

  26. #26
    Master Ruggertech's Avatar
    Join Date
    Jun 2019
    Location
    Deepest darkest South Wales.
    Posts
    7,210
    Quote Originally Posted by lewie View Post
    That’s the correct size for the condensation pipe- maybe yours is a different pipe- but if it’s is the condensation pipe it shouldn’t (I believe) be routed into the gutter
    Well no it shouldn't be directed into the gutter as I explained and ad I found out.

  27. #27
    Craftsman
    Join Date
    Nov 2013
    Location
    Leeds England
    Posts
    674
    Quote Originally Posted by walkerwek1958 View Post
    Got up this morning, ran the hot water tap and couldn't get hot water, at this point my day started to go downhill. Central heating boiler problems are an absolute pain, always occur at the least convenient time and like many I rely totally on a combi boiler to provide heating and hot water so when it packs up I`m screwed. Boiler's only 18 months old, problem turned out to be the condensate drain line blocked solid with bloody ice. Fortunately it's v. easy to get to, with approx. 3 feet running vertically down the bungalow wall into a drain. 15 mins with a hair dryer fixed it and the boiler's now running OK again.



    What I can`t work out is how to prevent this happening again, ideally the condensate line could've been run into the drain pipe from the dishwasher indoors, but now the kitchen's been refitted it's a sizeable job to modify so I`m stuck with the vertical pipe outside. Thought about lagging it but I`m not convinced it'll help, the temperature of the line follows the ambient cycle, warming above freezing (usually) in the daytime and dropping at night, if it's lagged it won't warm up as readily.

    After a couple of days of sub-zero temperatures with no sunlight the line has blocked and I see no reason why it won't happen again, despite it being a simple problem to understand I`m struggling to find a solution.

    If this was in an industrial setting the line would be trace heated and lagged, problem solved, I find domestic plumbing frustrating in this respect !.



    All suggestions welcome. Modifying the line to make it easy to dismantle and allow the condensate to drip freely when the temp is sub-zero is one answer but it's hardly subtle.

    That external pipe should be a minimum of 32mm and lagged if running outside.
    I think its Tubolit or Armaflex that do external lagging that is suitable .

  28. #28
    Plenty of lagging on Amazon.

  29. #29
    Think most options have already been covered here but for what it’s worth.

    We use 32mm for outside condense runs, if you do this and use a suitable condensate lagging it SHOULD be fine. If you want to leave and use the existing pipe, the most successful option we have seen is and boxing in with lagging / insulation.

    Under extreme weather conditions there is always a risk of freezing and running internally should always be the preferred method.

    As already said, trace heaters can also work very well.

  30. #30
    Grand Master
    Join Date
    Jul 2007
    Location
    Wakefield, West Yorkshire
    Posts
    22,521
    Just returned home after an evening of 'socialising', taken the dog for a short walk, it's absolutely bitter cold outside! Hopefully this problem won't re-occur but the ambient temp is definitely sub-zero.

    Had a think about this problem, if I drill a small (2mm) hole in the top of the protruding horizontal section of pipe this should prevent the boiler sensing a blockage, even if the vertical leg becomes blocked with ice. Can`t see why this shouldn't work as a short-term solution. If the 1 metre long vertical section becomes totally full of ice we'll be into a full-blown Arctic winter...........I thought global warming was supposed to avoid this scenario!

    Thanks to all who've contributed with comments and suggestions.

  31. #31
    Master blackal's Avatar
    Join Date
    Mar 2012
    Location
    Scottish Borders
    Posts
    9,796
    Acidic water may spray on the brickwork…………

    that might be an issue?

  32. #32
    Master
    Join Date
    Aug 2010
    Location
    Kent
    Posts
    7,282
    Quote Originally Posted by blackal View Post
    Acidic water may spray on the brickwork…………

    that might be an issue?
    Yeh my daughters had a small hole in it and found it’s way onto a nearby copper pipe - burnt clean through the copper

  33. #33
    Grand Master learningtofly's Avatar
    Join Date
    Jul 2010
    Location
    Everywhere & nowhere, baby
    Posts
    37,607
    Is the lagging split in order to get it on the pipe, and does it then need some kind of external wrap to seal it?

  34. #34
    Quote Originally Posted by learningtofly View Post
    Is the lagging split in order to get it on the pipe, and does it then need some kind of external wrap to seal it?
    Yes, split and usually self-adhesive. Look at these https://amazon.co.uk/s?k=condensate+pipe+lagging

    Obv. choose one suitable for outside.

  35. #35
    Grand Master learningtofly's Avatar
    Join Date
    Jul 2010
    Location
    Everywhere & nowhere, baby
    Posts
    37,607
    Quote Originally Posted by Kingstepper View Post
    Yes, split and usually self-adhesive. Look at these https://amazon.co.uk/s?k=condensate+pipe+lagging

    Obv. choose one suitable for outside.
    Thank you.

  36. #36
    Grand Master Onelasttime's Avatar
    Join Date
    Oct 2014
    Location
    Everywhere, yet nowhere...
    Posts
    13,881
    What I don't understand is why this problem isn't accounted for at the time of fitting?

    Surely it's pretty common over winter so why not ensure the pipe is properly protected against freezing in the first place rather than leave the homeowner to figure it out while sitting in their freezing cold house?

    Any heating engineers care to shed light on this?

  37. #37
    Master
    Join Date
    Dec 2008
    Location
    Winchester
    Posts
    2,215
    Another current thread on same topic https://forum.tz-uk.com/showthread.p...-outside-pipes

  38. #38
    Master blackie's Avatar
    Join Date
    Oct 2010
    Location
    Up north wit cowd weather
    Posts
    4,222
    We use trace heating at work. It's normally about 5w per mtr and you can cut and seal one end and make off the other to accept a plug with shrink-wrap.
    Obviously fused down correctly.
    I used a full coil once in the filter of a koi pond to keep the chill off.
    It's easy stuff to work with providing the ends get the correct seal

  39. #39
    Master Franco's Avatar
    Join Date
    Mar 2003
    Location
    South Yorkshire
    Posts
    1,362
    Blog Entries
    1
    In my old house there was something like this installed:

    https://www.tlc-direct.co.uk/Products/BNPW03.html

    The good thing is that the heating of the pipe starts when temps are below 3-4 degrees - regulates itself. And did work very well.

    You can keep it unplugged most of the year, then on when temperatures drop.

  40. #40
    Craftsman
    Join Date
    Oct 2003
    Location
    Lancaster / Stavanger / Fishguard, Norway / UK
    Posts
    495
    I used pipe insulation on mine after a similar event in the beast from the east and, fingers crossed, it has never repeated since doing that. Never been as cold as that mind you but I am pretty confident.


    Sent from my iPhone using Tapatalk

  41. #41
    Master
    Join Date
    Apr 2006
    Location
    Berkshire
    Posts
    5,123
    Just happened to me for the first time this morning. Only noticed as the utility room where the boiler etc are located had a wet floor.
    Wasn’t sure what caused it but thought to look outside and sure enough could see the end of an ice plug at the bottom of the pipe.
    10 mins with a hair dryer and then a thin drain cleaner up the pipe and the block of ice fell out.
    Now re-reading this thread to work out a long term solution.
    First time this has happened though so maybe we’ve been lucky.

  42. #42
    Master
    Join Date
    Jan 2017
    Location
    Wolverhampton
    Posts
    4,232
    Quote Originally Posted by Onelasttime View Post
    What I don't understand is why this problem isn't accounted for at the time of fitting?

    Surely it's pretty common over winter so why not ensure the pipe is properly protected against freezing in the first place rather than leave the homeowner to figure it out while sitting in their freezing cold house?

    Any heating engineers care to shed light on this?
    Obviously I'm not a heating expert but after recent events 'gifted amateur' might be on the horizon lol.
    Plumbers do know about these problems but some are lazy buggers and others are loathe to suggest cost increases on already expensive builds. Also if the refit is replacement of an old boiler and/or immersion system (also warm air system as in the case of my Daughter's house) there is just not the provision for supplementary drainage.

  43. #43
    Craftsman
    Join Date
    Oct 2020
    Location
    UK
    Posts
    703
    My Worcester Greenstar combo boiler stopped working yesterday evening - error code 227. The boiler is 12 months old. I suspect it is a frozen condensate pipe (-10 last night) which runs down the outside of the house from the first floor to the ground, and is not lagged. I don’t fancy trying to thaw several meters of pipe using a hair dryer. I can’t reach the top half anyway. I think I am going to have to suffer until the thaw on Sunday.

    It is really cold in the house. No central heating, no hot water. Fortunately I have got two small oil filled heaters.

  44. #44
    a few tips here.


  45. #45
    Master blackal's Avatar
    Join Date
    Mar 2012
    Location
    Scottish Borders
    Posts
    9,796
    Quote Originally Posted by Tatters View Post
    My Worcester Greenstar combo boiler stopped working yesterday evening - error code 227. The boiler is 12 months old. I suspect it is a frozen condensate pipe (-10 last night) which runs down the outside of the house from the first floor to the ground, and is not lagged. I don’t fancy trying to thaw several meters of pipe using a hair dryer. I can’t reach the top half anyway. I think I am going to have to suffer until the thaw on Sunday.

    It is really cold in the house. No central heating, no hot water. Fortunately I have got two small oil filled heaters.
    That code is for flame failure (or flame establish).

    Might be condensate line, but.................... Better to find out now rather than hope for the best?

  46. #46
    Grand Master Onelasttime's Avatar
    Join Date
    Oct 2014
    Location
    Everywhere, yet nowhere...
    Posts
    13,881
    Quote Originally Posted by Tatters View Post
    My Worcester Greenstar combo boiler stopped working yesterday evening - error code 227. The boiler is 12 months old. I suspect it is a frozen condensate pipe (-10 last night) which runs down the outside of the house from the first floor to the ground, and is not lagged. I don’t fancy trying to thaw several meters of pipe using a hair dryer. I can’t reach the top half anyway. I think I am going to have to suffer until the thaw on Sunday.

    It is really cold in the house. No central heating, no hot water. Fortunately I have got two small oil filled heaters.
    If it's any consolation, I had a problem a couple of years ago with a WB Greenstar boiler still in warranty, and WB were brilliant, sending engineers the next day and fixing the problem. The female engineer was pretty fit as well, which was a bonus.

    Good luck. At least the weather is set to become milder over the weekend.

  47. #47
    Master
    Join Date
    Jan 2017
    Location
    Wolverhampton
    Posts
    4,232
    Quote Originally Posted by Tatters View Post
    My Worcester Greenstar combo boiler stopped working yesterday evening - error code 227. The boiler is 12 months old. I suspect it is a frozen condensate pipe (-10 last night) which runs down the outside of the house from the first floor to the ground, and is not lagged. I don’t fancy trying to thaw several meters of pipe using a hair dryer. I can’t reach the top half anyway. I think I am going to have to suffer until the thaw on Sunday.

    It is really cold in the house. No central heating, no hot water. Fortunately I have got two small oil filled heaters.
    If you can identify the outlet pipe, seperate it inside the house - assuming it is a plastic pipe like ours - then attach some hose or pipe to empty the condensate into a bucket. At least you can temporarily get your hot water back until a more permanent solution is possible.

  48. #48
    Craftsman
    Join Date
    Oct 2020
    Location
    UK
    Posts
    703
    Thanks for the suggestions, I will have time tomorrow to look at it. I am waiting until the better weather on Sunday to see whether I need to call out an engineer - I imagine they are very busy now, and I won’t be able to get anyone for some days anyway.

  49. #49
    Master
    Join Date
    Feb 2015
    Location
    London, UK
    Posts
    3,037
    Yep mine has frozen too. Well, the condensate pipe itself hasn’t, but the plastic pipe work it drains into outside has. This is shared with the washing machine waste and caused a minor flood earlier, thankfully the Mrs was in the vicinity and managed to prevent disaster.

    I have a bit of a workaround so we can still have shortish blasts of heating and hot water. But I’ll work out a proper fix when it has all defrosted on Sunday (hopefully!).

    I’m over this cold blast now. Bring on our usual wet, mild Christmas!

  50. #50
    Master
    Join Date
    Sep 2007
    Location
    SUNNY BRISTOL
    Posts
    3,296
    I had this very problem and my plumber suggested a pump. All the condensate drains into the pump which is located below the boiler indoors, once it full the pump kicks in and it goes thru the pipe under pressure to the outside drain. No residue is left in the pipe so no icing up can occur outside of the building, easy to install about an hours work and the pump was around £100.