Thread: Bifold Doors Flush with Inside Floor and Patio

  1. #1

    Bifold Doors Flush with Inside Floor and Patio

    We are having a rear extension next month and having ubiquitous bifold doors.

    We would like seamless transition from the inside of the house to the patio. Effectively the inside floor bifold sand patio are all flush, to create the appearance of a single space flowing into the garden.

    The structural engineer came around yesterday to measure up for the structural plans and did not recommend this as he said it is very difficult to make the bifold truly weatherproof.

    Anyone have this set up and can comment with their experience?

  2. #2

  3. #3
    Master
    Join Date
    Apr 2012
    Location
    Surrey, UK
    Posts
    2,632
    We received the very same advice when having our bifolds installed and I can see the sense in it. We have a very small lip (approximately 1-inch) and it doesn't detract or seem to cause us any issues at all.

  4. #4
    Master
    Join Date
    Sep 2008
    Location
    Wirral
    Posts
    4,729
    I have clients who ask for this all the time and recommend against it. It’s fine in the Med but here we just don’t have the climate. So far as I know there are no door companies that will guarantee a water tight flush cill in the UK. You can bring your patio up level with the internal finished floor level with a normal low threshold cill but make sure there is some form of permeable break between the door frame and pavings. For example an Aco channel or loose stones. Obviously don’t bridge your DPC whilst don’t this.

    The one client I did have who went against the advice of the door company and fitted a flush cill did have leaks from time to time.
    Last edited by benny.c; 19th May 2018 at 11:32.

  5. #5
    Grand Master TheFlyingBanana's Avatar
    Join Date
    Mar 2009
    Location
    Bedfordshire and your back garden
    Posts
    23,188
    Quote Originally Posted by noTAGlove View Post
    We are having a rear extension next month and having ubiquitous bifold doors.

    We would like seamless transition from the inside of the house to the patio. Effectively the inside floor bifold sand patio are all flush, to create the appearance of a single space flowing into the garden.

    The structural engineer came around yesterday to measure up for the structural plans and did not recommend this as he said it is very difficult to make the bifold truly weatherproof.

    Anyone have this set up and can comment with their experience?
    i don’t know of anyone who has had exactly what you suggest done, for precisely the reason you were given. I guess if there was a gentle slope away from the doors it might be possible f you are determined.
    So clever my foot fell off.

  6. #6
    Thanks. I’ve just got some technical drawings from Kloeber, one company we are considering.

    They illustrate a 74 mm (3”) lip above the finished floor level. Is this a little on the large side?

  7. #7
    Master
    Join Date
    Apr 2012
    Location
    Surrey, UK
    Posts
    2,632
    Quote Originally Posted by noTAGlove View Post
    Thanks. I’ve just got some technical drawings from Kloeber, one company we are considering.

    They illustrate a 74 mm (3”) lip above the finished floor level. Is this a little on the large side?
    Are you kidding! 3" is gimoungous, at least that's what I've always thought...

    In all seriousness though yes that does sound a little on the large side, like I said we've got no more than about 1-1.5" and it's just right.
    Last edited by MST; 19th May 2018 at 11:49.

  8. #8
    My house has them. The doors were already here when I bought the house and were installed 8 years ago.

    They’re from

    https://www.foldingslidingdoors.com/

    I have a patio outside and have never had any issues at all in the 18 months I’ve lived here . With kids I much prefer it over the step down I had in my old house as they run in and out of the house and don’t have to worry about tripping up.

    If I was fitting them again I would do them as they are.

  9. #9
    Here's the technical drawing I have from Kloeber. As you can see it's a 74 mm lip from the top of the inside finished floor and a 88 mm (129 -41) lip from the top of the outside patio

    The structural engineer was also concerned that the patio was above the bottom plastic board. If we put the plastic below this then the lip to patio would be 162 mm (129 + 10 + 26) or nearly 6.5" in old money.

    What's the thoughts on this? Can the patio be raised above the plastic bottom board? What's the best way to get it as flush a possible without compromising weather tightness, and which doors should we look at in that case?


  10. #10
    Master
    Join Date
    Apr 2012
    Location
    Surrey, UK
    Posts
    2,632
    Quote Originally Posted by noTAGlove View Post
    What's the thoughts on this? Can the patio be raised above the plastic bottom board? What's the best way to get it as flush a possible without compromising weather tightness, and which doors should we look at in that case?

    Ours is and it doesn't seem to cause an issue, we've got Schüco bifolds and our understanding, having been to a Kloeber showroom, was that they are just rebranded Schücos.

  11. #11
    Origin are good,the cull on the drawing won’t be there as you would order them without it ,we always do them so there about 20mm higher than the patio and put a slot drain in front


    Sent from my iPhone using Tapatalk

  12. #12
    Quote Originally Posted by MST View Post
    having been to a Kloeber showroom, was that they are just rebranded Schücos.
    Any details behind that? Schucos are much more expensive than Kloeber.

  13. #13
    Craftsman Nuisance Value's Avatar
    Join Date
    Jan 2015
    Location
    Central Scotland
    Posts
    682
    Quote Originally Posted by noTAGlove View Post
    Here's the technical drawing I have from Kloeber. As you can see it's a 74 mm lip from the top of the inside finished floor and a 88 mm (129 -41) lip from the top of the outside patio

    The structural engineer was also concerned that the patio was above the bottom plastic board. If we put the plastic below this then the lip to patio would be 162 mm (129 + 10 + 26) or nearly 6.5" in old money.

    What's the thoughts on this? Can the patio be raised above the plastic bottom board? What's the best way to get it as flush a possible without compromising weather tightness, and which doors should we look at in that case?
    It's actually only a 5mm lip above the FFL. The 69mm is the folding door frame, so yes it will be 74mm when closed, but only 5mm when open.

    Besides, that looks like a sliding door section detail to me.. edit: Actually, could be bi-fold.

    In fact, you'll be struggling to better that and retain watertightness. If you look at the external level you would have 14mm between the internal and external FFLs with a 5mm lip on both. Pretty good.
    Last edited by Nuisance Value; 19th May 2018 at 15:40. Reason: misread drg; more detail

  14. #14
    Grand Master JasonM's Avatar
    Join Date
    Feb 2010
    Location
    Cambridgeshire
    Posts
    16,151
    Quote Originally Posted by Nuisance Value View Post
    It's actually only a 5mm lip above the FFL. The 69mm is the folding door frame, so yes it will be 74mm when closed, but only 5mm when open.

    Besides, that looks like a sliding door section detail to me..
    I thought that too looking at the numbers, but wasn't sure of myself to say.
    Cheers..
    Jase

  15. #15
    Master
    Join Date
    Apr 2012
    Location
    Surrey, UK
    Posts
    2,632
    Quote Originally Posted by noTAGlove View Post
    Any details behind that? Schucos are much more expensive than Kloeber.
    I actually thought it was the other way round!

    The main conclusions we came to when researching which ones to get was go aluminium, go German and DON'T have built in blinds.

    Inside - Outside



    Outside - Inside



    I've included our 2 year old's feet for the purposes of illustration! (model's own)
    Last edited by MST; 19th May 2018 at 18:12.

  16. #16
    Craftsman Nuisance Value's Avatar
    Join Date
    Jan 2015
    Location
    Central Scotland
    Posts
    682
    Quote Originally Posted by JasonM View Post
    I thought that too looking at the numbers, but wasn't sure of myself to say.
    We're right. I've just been through this with my own place and have spent hours checking sections to get the right heights on a sliding door install / window reveal sightlines etc.

    To add to this it's critical that the base course (external block leaf) and internal floor slab / screed / floor covering is bang on height wise, as this will determine the overall height it sits at.

    I'm sure I've read that it's good practice to sit folding doors on a steel beam, one to get the height right and secondly due to the forces / weight of the door leafs on folding doors do not overstress block / brick on the outer leaf. I know of one national house builder that won't fit them anymore due to this.

    It's not easy to get bang on.

  17. #17
    Master reggie747's Avatar
    Join Date
    Oct 2013
    Location
    The Mersey Riviera
    Posts
    7,200
    Quote Originally Posted by Nuisance Value View Post

    I'm sure I've read that it's good practice to sit folding doors on a steel beam, one to get the height right and secondly due to the forces / weight of the door leafs on folding doors do not overstress block / brick on the outer leaf.
    No, not at all.

  18. #18
    Craftsman Nuisance Value's Avatar
    Join Date
    Jan 2015
    Location
    Central Scotland
    Posts
    682
    Quote Originally Posted by reggie747 View Post
    No, not at all.
    No? I can't remember where I heard / read it..

  19. #19
    Master
    Join Date
    Apr 2012
    Location
    Surrey, UK
    Posts
    2,632
    Technical issues now resolved, please see the pics of our threshold in my reply above.

  20. #20
    Thanks all. 5 mm lip it is then.

    As a Chartered Engineer myself with some 27 years experience, you’d think I could read a technical drawing!

  21. #21
    Master yumma's Avatar
    Join Date
    Apr 2014
    Location
    Chelmsford, UK
    Posts
    2,987
    As a Surveyor, quick tip ask for the threshold to be wheelchair accessible or DDA compliant. It’ll most likely have a 12-15mm ramped threshold for weathering but that should be pretty good all round. Internal FFL and external GL can be the same level. Good luck.


    Sent from my iPhone using Tapatalk

  22. #22
    Master
    Join Date
    Feb 2014
    Location
    Leicester
    Posts
    1,166
    About half way through our rear extension project and gone with bespoke aluminium doors. Not that bothered about the seemless look TBH but will level the garden and probably go about 4 inch below the interior floor





  23. #23
    Journeyman
    Join Date
    Jul 2017
    Location
    South, U.K.
    Posts
    153
    Quote Originally Posted by noTAGlove View Post
    Here's the technical drawing I have from Kloeber. As you can see it's a 74 mm lip from the top of the inside finished floor and a 88 mm (129 -41) lip from the top of the outside patio

    The structural engineer was also concerned that the patio was above the bottom plastic board. If we put the plastic below this then the lip to patio would be 162 mm (129 + 10 + 26) or nearly 6.5" in old money.

    What's the thoughts on this? Can the patio be raised above the plastic bottom board? What's the best way to get it as flush a possible without compromising weather tightness, and which doors should we look at in that case?

    Just curious, you do realise the 74mm you quote in the drawing is from the finished floor to the top of the bottom rail on the door. When the door is open the threshold would only be 5mm above the floor. similarly the patio would only be a few mm below the outward side of the floor track. This is the best solution and there is no problem the patio being above the cil as long as the water can drain. IMHO this is a good way of achieving a low threshold without compromising the weatherproofing and we have fitted this several times with no problems